Here is what I can't wrap my mind around-- Kurt, with this type of fault, how can the set even pass a 3ph test? I have sold about dozen 5kw and 10kw sets over the last 6 years-- all of them I load tested the same way-- set reconnect to 3ph 120-208, hook via 4 wire connection to the a427a load...
Ok, so that means that there should be the correct number of loops since it loaded fully in the 120/208 3ph mode. Assuming that is the case, then the likely culprit are the two burden resistors not going into parallel via S8?
Kloppk gave me some more insights on how the monitoring works. Here is what he explained to me:
"There is a fault that can cause a 803A to pass a 208 3 phase load test but fail with an Overload fault when running 120/240 single phase. Namely in S8 contacts 13 to 14. In 120/240 S8 13 14 close...
I reached out to some of the experts here on this-- I will let them chime in here.
For background info, I load tested the genset using an essex a427a load bank, but I did so on 120/208 3ph as that is how the load bank is primarily configured. It passed with flying colors. I have since learned...