I was running my generator for an old timers reunion for my old NG unit when it just shut down. I restarted it and as soon as I released the start switch after holding it long enough for the oil pressure to build up it shuts down every time. I checked the oil pressure switch and it is good. A little history-- I was using a slave cable to start the gen. I did not have batteries in it but I did wrap the pos battery lead to prevent problems. Well as it turns out I wrapped the neg lead. (I know, should have put batteries in
). After the first start the amp gauge was showing the system was running at full charge. Now it shows nothing even with good batteries. Where do I go from here?

The wire going to the high temp switch was broken inside the insulation about 1 inch from the plug on the harness side. Nothing visible to let me know the wire was broken. I just started going through all of the wires testing continuity while pulling and twisting everything. Now I am off to get a couple hundred tie straps to bundle all of the wires like they were then I will put my newly insulated ASK back on. I stripped out the fiberglass and put in new armaflex foam.