Hello,
I have a MEP-804A and I have changed all the fluids and filters per manual. I go to start it and at first nothing on the front panel, I set the dead crank switch to normal and reset the 7.5A breaker behind the panel (it was out), now I have instrument lights, needles didn't seem to move on the panel, but I am not sure if that is normal. When I go to prime/aux, I can hear the aux pump run, prime and run, nothing, turn to start, and no crank. Dead crank switch works but does not light up the instrument lights when cranking so I am not sure that the correct systems are getting voltage.
I tried reading dc volts on the wire circled in the photo while the master was in crank position, nothing there.
Thank you in advance, this forum is a wealth of knowledge.

I have a MEP-804A and I have changed all the fluids and filters per manual. I go to start it and at first nothing on the front panel, I set the dead crank switch to normal and reset the 7.5A breaker behind the panel (it was out), now I have instrument lights, needles didn't seem to move on the panel, but I am not sure if that is normal. When I go to prime/aux, I can hear the aux pump run, prime and run, nothing, turn to start, and no crank. Dead crank switch works but does not light up the instrument lights when cranking so I am not sure that the correct systems are getting voltage.