• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

MEP-805 Frequency Fluctuation

Feenix206

New member
12
3
3
Location
Michigan
Latest: after finishing all above testing, and not changing anything the 804 A DS7 came on when S5 actuated and output at K1. Im confused i did nothing now it works. Question: does battery voltage come into play? When cold testing bat voltage was running about 22~23v. After all the test tuns it was up to 27v. However on this last failure to get voltage days ago, it happened after a 7hr run so bat voltage was at peak then.
 

peapvp

Well-known member
Steel Soldiers Supporter
1,326
1,731
113
Location
Basehor, KS
No, it wouldn’t make any difference.

you should have around 22V to 27V on the Anode Side when S1 Switch in Run/Prime Position

IMG_7697.png
this would be on Terminal 5 of S5
You should have 0.5 V less on Terminal 2 and on Terminal 3 of S5
You should also have this Voltage on K8 terminals 11 and 12 and on K13 terminals 7 and 1
If you test in this sequence then you are following the exact voltage path of this circuit.
It is not uncommon that the switches, terminals, relay sockets etc are dirty, corroded or loose. The S5 switch is also suspect to wear and so is K1 itself

Just removing one wire can make or brake a circuit, which may have happened here in your case and the thing started to work again for the moment
 

Feenix206

New member
12
3
3
Location
Michigan
No, it wouldn’t make any difference.

you should have around 22V to 27V on the Anode Side when S1 Switch in Run/Prime Position

View attachment 901953
this would be on Terminal 5 of S5
You should have 0.5 V less on Terminal 2 and on Terminal 3 of S5
You should also have this Voltage on K8 terminals 11 and 12 and on K13 terminals 7 and 1
If you test in this sequence then you are following the exact voltage path of this circuit.
It is not uncommon that the switches, terminals, relay sockets etc are dirty, corroded or loose. The S5 switch is also suspect to wear and so is K1 itself

Just removing one wire can make or brake a circuit, which may have happened here in your case and the thing started to work again for the moment




where might I find a complete wiring diagram that you pictured above. That would be helpful next time tracing down the path.
 
Top